Guys,
Electronics is my admitted weak suit (among others). By way of background, I bought a laundry unit early this year which had been in storage and contained a mep-003A with only 54 original hours, 1991 model on a 1991 laundry unit. Generator ran like a dream until the day SS website went down.
On that day I installed a battery isolator switch to the negative battery cable, patterning it off the unit I removed the switch from (which still runs great). In the process of installing the switch I arc'd the negative cable twice to the hold down frame (tiny sparks). On completion of switch installation I restarted the unit and no power. Did the following per TM:
(1) Isolate the trouble to generator or regulator.
Discomect the voltage regulator at the exciter (wires
P67C16 at TB3-5 and P60E16 at TB3-6). Connect a 12
volt battery in place of the regulator with the (+)
terminal to TB3-6 and (-) terminal to TB3-5. Run the
engine with the battery in place of the voltage regulator.
If there is output now, the voltage regulator is
bad. If there is no output, the main alternator is bad.
No power off the 12 volt battery, so....if TM is to be believed, my AC VR is fine but my little shorts killed the main alternator (gen head). I have had similar arcs in the past with no effect. I hate to tear into the diodes and other fearful areas. 10 amp fuse is fine on the DC side in case you wonder and should have no effect anyway.
I then removed the switch and returned the unit to original configuration. No change, still no juice.
Does anyone have any suggestions? I can't see how this experience could have caused damage anywhere except possibly the AC VR. I am not too hot on the idea of testing it either but will do whatever unless someone raises their hand.
Thanks in advance for the sage advice which I'm sure will spew forth. Golly, I'm glad this board is back up! Cheers Patracy!
Jerry
Electronics is my admitted weak suit (among others). By way of background, I bought a laundry unit early this year which had been in storage and contained a mep-003A with only 54 original hours, 1991 model on a 1991 laundry unit. Generator ran like a dream until the day SS website went down.
On that day I installed a battery isolator switch to the negative battery cable, patterning it off the unit I removed the switch from (which still runs great). In the process of installing the switch I arc'd the negative cable twice to the hold down frame (tiny sparks). On completion of switch installation I restarted the unit and no power. Did the following per TM:
(1) Isolate the trouble to generator or regulator.
Discomect the voltage regulator at the exciter (wires
P67C16 at TB3-5 and P60E16 at TB3-6). Connect a 12
volt battery in place of the regulator with the (+)
terminal to TB3-6 and (-) terminal to TB3-5. Run the
engine with the battery in place of the voltage regulator.
If there is output now, the voltage regulator is
bad. If there is no output, the main alternator is bad.
No power off the 12 volt battery, so....if TM is to be believed, my AC VR is fine but my little shorts killed the main alternator (gen head). I have had similar arcs in the past with no effect. I hate to tear into the diodes and other fearful areas. 10 amp fuse is fine on the DC side in case you wonder and should have no effect anyway.
I then removed the switch and returned the unit to original configuration. No change, still no juice.
Does anyone have any suggestions? I can't see how this experience could have caused damage anywhere except possibly the AC VR. I am not too hot on the idea of testing it either but will do whatever unless someone raises their hand.
Thanks in advance for the sage advice which I'm sure will spew forth. Golly, I'm glad this board is back up! Cheers Patracy!
Jerry