Howdy,For load testing this prior to hooking up to the house, I should be able to hook the ground to the already driven ground rod, and ensure neutral and ground are tied tougher at the generator right? I know that when it comes time to connect to the house, generator ground needs to connect to house ground, and generator neutral needs to be floating.
Daybreak,Howdy,
Generator running by itself= ground rod, wire to ground lug, bonding strap in place (flat copper plate next to neutral lug)
Generator connected to house= bonding strap removed, all four wires connected to house. (single phase 120/240) The ground neutral bonding is already in place at your panel.
Yup, 3650 MW thermal, 1280 MW electric.You sure its not 1.21 jiga-watts?![]()
I picked it up today.Yup, 3650 MW thermal, 1280 MW electric.
Good luck with your unit tomorrow, hope it's a runner with no issues.
That's awesome Chris, glad to hear she's a runner with no issues. What did you end up paying if you don't mind me asking?I picked it up today.
The generator has a bit of a bash on its top from something hitting it pretty hard. I took it apart to make sure there wasn't any hidden damage. There wasn't. Cosmetic only. The particular generator came with fluids still in it and a set of batteries. The power cables were still tied up as it comes from the factory. I even have the ground rod kit and the AUX fuel hose. Its a Tier2 reset from 2012.
I checked the batteries and they each showed 12.1v. Ok. Not bad. After a short charge they were up to spec.
Next I decided to turn it over with the dead crank switch to make sure nothing was binding. It spun easily and nothing sounded wrong.
Now the moment of truth. I primed the fuel system and hit the start button. It IMMEDIATELY fired and ran perfectly. It didn't make a full revolution on the starter before it popped off and ran.
I'm letting it run a little bit and everything is just as it should be except for one thing, the sound.. This thing is a LOT quieter than my MEP003a. Its quieter with the covers OFF than the MEP003 is with the ASK.
I'm going to have a hard time parting with this one. I may end up keeping it.
Holy smokes, prices have gone up quite a bit when I picked mine up for $3800 back in February, and SWMBO gave me a load of grief on that amount. That said, I likely would've paid what you paid to end up with a unit in the condition it's in.Probably too much to be able to resell it. With fees and taxes about $5100.