• Steel Soldiers now has a few new forums, read more about it at: New Munitions Forums!

  • Microsoft MSN, Live, Hotmail, Outlook email users may not be receiving emails. We are working to resolve this issue. Please add support@steelsoldiers.com to your trusted contacts.

MEP 002a Not producing Electricity, I am looking for someone who is familiar with the 002a to work on it.

chb32nj

Member
31
42
18
Location
Chatsworth, NJ
We have no rats in NJ, well as long as you don't consider the government. :LOL: :LOL:
One thing we do have an abundance of is chipmunks and they will go up the exhaust and actually store food past the open valves on top of pistons.
Rick, We might have a couple of rats in NJ!! Lol!

Just want to give everyone a quick update. I found a Generator Tech from a local repair business that is very familiar with the Onan DJ series and rotating diodes. He will be stopping by in a week or 2 and take a look at it. I will keep everyone informed when he stops by and hopefully make some progress.

I want to thank everyone for all the help and suggestions! I greatly appreciate it!
 

chb32nj

Member
31
42
18
Location
Chatsworth, NJ
Rick, We might have a couple of rats in NJ!! Lol!

Just want to give everyone a quick update. I found a Generator Tech from a local repair business that is very familiar with the Onan DJ series and rotating diodes. He will be stopping by in a week or 2 and take a look at it. I will keep everyone informed when he stops by and hopefully make some progress.

I want to thank everyone for all the help and suggestions! I greatly appreciate it!
 

chb32nj

Member
31
42
18
Location
Chatsworth, NJ
I have an update on my 002a not producing power. First I want to thank everyone here for all the help you have given to me!
And a big shout out and thank you to Ray70 for rebuilding the IP on my MEP002a Gen #2. Runs Perfect now!
The Gen Tech that was going to stop by and check the diodes never showed up.
After reading the TM and a couple of threads I checked the diodes myself. I unbolted them 1 at a time and checked the resistance with my multi meter, which to my surprise had a diode test function. Every one tested ok, I think! Nothing one way and when I reversed it showed resistance. I am attaching pictures in case I am not stating what I did correctly. 3 pictures are from F1 and 3 are from F2. Not sure what to do next.
 

Attachments

Ray70

Well-known member
Steel Soldiers Supporter
2,858
6,919
113
Location
West greenwich/RI
To add a little bit more info to Chris' post above, while he was here in RI we swapped out both the control cube and AC reconnection box with no change. This is also what led us to both feel that the previous post about the rotating diodes being the problem were most likely correct. At this point I would still say the problem is most likely somewhere within the generator head itself.
Best thing I can suggest is a close inspection of the wiring going to the generator, paying closest attention to the plug with the 2 small wires. I know the wiring on that machine looked good, but pay close attention to things like corrosion or damaged pin sockets in the mating plugs.
Also, see what can be seen within the gen head itself as far as wiring connections to be sure everything is good. Also follow the instruction in the TM to check the winding resistances of the generator, this resistance test would definitely help highlight any internal shorts or opens in the windings.
 

Guyfang

Moderator
Staff member
Moderator
17,774
26,511
113
Location
Burgkunstadt, Germany
The small connector going to the main gen should be J12? Pins A&B are the F1 and F2 wires, that provide the initial excitation. Pin A is P67B and Pin B is P60G. Take the plug off, and Test at the two pins while someone else tries to start the gen set. Even after it starts, hold up the S1. you should get 24 VDC, I think. If you get no DC voltage, the main gen can not light off.
 

chb32nj

Member
31
42
18
Location
Chatsworth, NJ
I was able to check the winding resistance on the generator today. Nothing good to report. I did not get 1 good reading. Everything was either 0 or open circuit. I thought at least one circuit would have some resistance. I am attaching a chart of the circuits tested and the results. I think I should just look for a different Generator head and change it out. Thanks again to everyone for all your help! Very much appreciated!

1/10/2021-This is an edit to make a correction to the chart. See post #74 for an updated chart. Here is the correction; Test #5 is T2 & T5 which is P9D and P10F. When I wrote down all the crossovers from wire to plug position I made a mistake for T5 and listed it as P9F instead of P10F. Sorry for any confusion.
 

Attachments

Last edited:

Ray70

Well-known member
Steel Soldiers Supporter
2,858
6,919
113
Location
West greenwich/RI
If those readings are correct your gen head is a gonner. I can see getting readings that are maybe an ohm off, simply due to differences in meters and resistance in your leads, but all open and shorted circuits would seem to indicate catastrophic damage.
 

Ray70

Well-known member
Steel Soldiers Supporter
2,858
6,919
113
Location
West greenwich/RI
Maybe I'm reading the numbers wrong, but reading #15 P10-A looks like a direct short, doesn't it?
The manual says all readings of P9 and P10 to A-F should all be high. A low resistance on any of them should be signs of a shorted rotor shouldn't it?
 

Guyfang

Moderator
Staff member
Moderator
17,774
26,511
113
Location
Burgkunstadt, Germany
I have been looking at the diagrams, till my eyes run. Both you and the OP are saying P10-A. I see a J10-A. Do we agree thats the same thing? P is the plug side. J is the jack side?
 

Ray70

Well-known member
Steel Soldiers Supporter
2,858
6,919
113
Location
West greenwich/RI
Must be the same thing. I'm looking in the TM procedure and it says P10, and the image on page 159 shows the plugs on the gen head being labeled P9 and P10...
These are the 2 main power output plugs coming off the gen head.
I'd assume the mating plugs on the AC reconnect box are J9 and J10.
 

Ray70

Well-known member
Steel Soldiers Supporter
2,858
6,919
113
Location
West greenwich/RI
Ah, as usual, you are correct! P10-A goes to X13A8 ground wire. There is a mistake on page 152 paragraph 2 on the right, winding resistance testing. It says P9 and 10 A-F. Should be P10 B-G with A being a ground!
Good work looking at the schematic Guy!
Now... back to analyzing Chris' other reading.... :)
 

Ray70

Well-known member
Steel Soldiers Supporter
2,858
6,919
113
Location
West greenwich/RI
What about all the winding resistance readings, should be 3.3 ohms on all 6 and he is getting 0 ohms across all?
Wouldn't that have to either be 6 incorrect readings or shorts within the windings?
 

Guyfang

Moderator
Staff member
Moderator
17,774
26,511
113
Location
Burgkunstadt, Germany
OK, lets agree that 13-15 test are good to go.
Then test 10-12 should be good.

Test 1-3. You should get no continuity, between T1 and T2, or T2 and T3, or T1 and T3. They are not a pair. So they should be open. Those tests should be GOOD.

That leaves test 4-9. Here I see a problem,


These are the wire pairs, for the phases. T2 to T5 is NOT a good reading. I seem to remember that its a PITA to take these readings, and I had to do it several times to make sure I had the right pins. I would do this again, to be sure.

The J12 plug test is also good.

What about all the winding resistance readings, should be 3.3 ohms on all 6 and he is getting 0 ohms across all?
Wouldn't that have to either be 6 incorrect readings or shorts within the winding?
When I did these tests back about a million years ago. We used a Wheatstone Bridge. Is a Multimeter made to todays standards, as good as a wheatstone bridge? I also thing the readings are to be taken at 25 degrees CELCIUS.
 

rickf

Well-known member
Steel Soldiers Supporter
3,331
2,220
113
Location
Pemberton, N.J.
Correct me if I am wrong but if it had shorted on ALL of the windings then it would have let out a LOT of magic smoke and it would certainly smell like it did.
 